Many drive choices are available from a variety of vendors, so some of the basics and best
practices are important to follow.
By Tom Stevic, contributing editor
May 27, 2016

Print Email Tweet Share Share

- A A A A +

About the author


Thomas Stevic is a controls engineer at Star Manufacturing, an engineering and
production company in Cincinnati. Contact him at tstevic@putman.net.

When choosing a variable frequency drive (VFD), several decisions must be made
besides the obvious voltage and current selections. Even the name should be decided
on, as it is often called a variable speed drive, adjustable speed drive, micro drive and
inverter.

In general, a VFD takes an ac power source and converts it into dc power. The speed control portion of the
drive uses the dc voltage to create dc pulses in varying frequency to drive the output motor at speeds other
than the 3,600 rpm or 1,800 rpm or other speed depending upon the number of poles the motor was designed
to operate at using a 60 or 50 Hz ac supply voltage.

How big should the VFD be? The size of the VFD should be chosen based on maximum motor current at peak
demand and not chosen based upon motor horsepower. Constant starting, stopping and dynamic loads
affects the electronics inside the VFD far more than the effect they have upon the local power bus and a full
voltage motor starter. Therefore, peak demand current should be used. Manufacturers may continue to list hp
ratings more as an historical rating than as a useful one.

Perhaps the first decision to make when choosing a VFD is to pick between a voltage/frequency (V/F or
V/Hz) drive and a vector controller. Both control methods may or may not be used with feedback such as a

1 of 6 04/09/2016 6:17
How to select a variable frequency drive https://www.controldesign.com/articles/2016/how-to-select-a-variable-...

rotary encoder. In general, most VFD-controlled motors are operated in an open-loop scenario but take
advantage of the VFDs soft start and adjustable speed features.

Also read: Peter Hammond recalls the birth of the medium-voltage drive

The V/F controller is simpler and often lower in cost than the vector controller in VFD applications. The V/F
controller works well if the load is rather constant and the speed is set high enough to prevent overheating of
the motor. A V/F drive is typically set up to use one of several preprogrammed V/F patterns that are designed
for specific applications such as a variable torque fan or pump application. Applications such as conveyors
and hoists may be programmed to use a constant torque V/F pattern.

Vector control provides a more dynamic control of the motor. By


independently controlling the output frequency and torque, the vector-
controlled motor can be programmed to limit the torque applied by a motor
The size of
shaft to prevent tool breakage in a drilling application and to provide a
the VFD steady speed for a conveyor independent of load. To properly utilize the
should be vector control advantages and operate at the best efficiency, the drive
chosen based must be set up with the proper motor characteristics and requires tuning
on maximum the drive to the system dynamics.
motor current
at peak VFDs decelerate motors at a programmable rate. As the load increases
demand and and the stop time decreases, the motor becomes a generator, often
not chosen causing overvoltage faults on the drive. Adding an external braking resistor
eliminates this problem by turning the regenerated voltage into thermal
based upon energy. Applications with high inertia, high motor loads or loads fighting
motor gravity often require external braking resistors that will need to be sized
horsepower. properly. The heat will also need to be dissipated, often outside a control
enclosure, so the braking resistors mounting location and guarding from
thermal and voltage hazards must be considered carefully.

All VFDs create harmonic noise voltage, and it gets worse as the drive load increases. The noise on the
input, line side of the drive can be fed back into the plant power distribution system, so it is a good design
practice to use input filtering. The filters are often available from the drive vendor or from third-party suppliers.

VFDs sold in Europe have much more stringent filtering requirements then those sold in the United States and
other locations. Both passive and active filters are available to help mitigate this noise. If harmonic noise is
suspected, or perhaps even as a general installation process, power quality meters are available that can
measure the quality of the power system before and after the installation of a VFD.

On the output side of the controller, line reactors help to protect the wiring and motor from excessive
electrical noise. If the system has power cable between the controller and the motor that is more than 50 ft
(15 m) or if the motor is non-inverter-rated, an output line reactor is almost a necessity.

The cabling used to power a motor with a VFD deserves some consideration. The cables will radiate
electrical noise and induce voltages in surrounding wire and cabling. A low-cost improvement would be to use
shielded and grounded cables. Choosing XLPE insulation as opposed to PVC offers a better dielectric
constant and high resistance, although it is less flexible. A low capacitance cable is also desired. By all
means, VFD motor cabling should always be routed away from any dc control voltage.

A VFD will work with a synchronous motor, but the most common installations will use three-phase induction
motors. Although general purpose induction motors may be controlled by VFDs, it's a poor design choice for
many reasons. Instead, use inverter duty motors as they can operate at a slower speed without overheating.
Plus the internal wiring insulation of an inverter duty motor is designed to withstand greater voltage spikes.
Although inverter duty motors are also more expensive, they are the proper choice for use with VFDs.

VFDs have become almost a commodity item in control system design. A quick and dirty speed control can

2 of 6 04/09/2016 6:17
How to select a variable frequency drive https://www.controldesign.com/articles/2016/how-to-select-a-variable-...

be purchased as a no-name VFD on the Internet for very little money. If the design requires greater reliability
and longevity, it would be wise to pick a product that has a history of reliability and good support. One would
hope that the more money spent on a VFD, the better quality the product. This is not always the case.

Major, well-known, controls manufacturers quite often private-label the products they build. In many cases,
the same controller can be purchased for less money buying it from the manufacturer than buying it from
another company that simply puts its brand name on the case. But a designer must also factor in support
levels both locally and at the end users facility. Having field support costs manufacturers money and does
add value to a product.

VFDs have a wide variety of programmable functions. Not all manufacturers call these functions by the same
name. Research is required to properly utilize a VFD to its best performance. We are fortunate to live in an
age where a great wealth of information is available on the Internet. Utilizing manufacturers websites and
educational information, plus a little time, can make most any controls person an expert in VFD selection.

RELATED: Read our report on the latest trends in motors and drives

Homepage image courtesy of Stuart Miles at FreeDigitalPhotos.net

Hide Comments

Join the discussion


We welcome your thoughtful comments.
All comments will display your user name.

Comments

Upload image

Comments
Submitted by Don Fitchett on Thu, 06/02/2016 - 17:24
A great one Thomas, thanks.

Reply
Submitted by on Sun, 07/03/2016 - 22:19
Make sure the VFD supports digital networking like PROFIBUS for the control and feedback signals as
opposed to using hardwired signals. Using networking you dramatically reduce the number of wires
required and I/O cards. Networking also enables intelligent device management (IDM) such as centralized
drive configuration and diagnostics. Learn more about IDM here: http://www.eddl.org/DeviceManagement/
Reply
Submitted by Nicholas J. Baranyk on Fri, 08/12/2016 - 07:07
It is a great article. One comment, however, which concerns me is the one saying that a VFD will work
with a synchronous motor. Depending upon the drive controller manufacturer, this may, or may not be the

3 of 6 04/09/2016 6:17
How to select a variable frequency drive https://www.controldesign.com/articles/2016/how-to-select-a-variable-...

case, as a synchronous motor will seamlessly transition between motoring, and regeneration. One might
think that such a motor would result in easy, predictable control, but in reality, you can cause yourself
headaches. By choosing a synchronous motor, you've already forced yourself into having snubbing /
regeneration capacity available, unless you can tolerate an excessive deceleration rate at a minimum. In
closing, I thank the author for taking the time for a terrific commentary.

Reply

RSS feed for comments on this page | RSS feed for all comments

Related Content

How do I synchronize conveyor speeds?


Variable frequency drive opens many options.

How to conserve energy and reduce noise with VFD cabling


Matching the proper cable to your VFD installation ensures reliable operation for the long

Energy-Saving Mechanicals for Machine Automation


A New Analysis From Frost & Sullivan is a Reminder That There Are Lots of Other Ways to

Drives Integrate, Gain Intelligence


Motors and Electronic Drives Evolve to Improve End Users' Machines and Applications

Most Popular
Past 7 Days Past 30 Days Past 6 Months All Time

01 Cybersecurity means protecting assets from remote-access threats


It is obvious that IIoT is going to create a bastion of security issues

02 NI announces CEO transition plan; board appoints new president


Alex Davern will succeed Dr. James Truchard, who has served as the CEO of

03 SCADA Systems: The heart and brain of industrial automation


Digitalization of information and increasingly pervasive internet

04 The IoT starts with common and proper things


Trillions of things are getting lost in the Internet of things (IoT), big

4 of 6 04/09/2016 6:17
How to select a variable frequency drive https://www.controldesign.com/articles/2016/how-to-select-a-variable-...

05 Motion Industries to acquire OBBCO Safety & Supply


OBBCO Safety & Supply is an industrial safety distributor.

About
Contact Us
Advertise
Media Kit
Rates & Spec
Privacy Policy
Legal / T&C

Content
Voices
Blogs
News
White Papers
Multimedia
Special Reports
Events
Products
Technology Roundups
E-lits
Vendor News

Magazine
Subscribe
Digital Edition
Issue Archive
Reprints

Site Tools
Knowledge Center
Company Profiles
Site Map

Stay Connected
My Account

5 of 6 04/09/2016 6:17
How to select a variable frequency drive https://www.controldesign.com/articles/2016/how-to-select-a-variable-...

Newsletters
RSS
Twitter
Facebook
Google+
LinkedIn
YouTube

Contact Us | Advertise | Privacy Policy | Legal Disclaimers, Terms & Conditions


Copyright 2004 - 2016 Control Design. All rights reserved.
P: 630-467-1300 | 1501 E. Woodfield Road, Suite 400N, Schaumburg, IL 60173

Chemical Processing | Control | Control Design | Food Processing | Pharmaceutical Manufacturing | Plant Services | Smart
Industry

6 of 6 04/09/2016 6:17

You might also like