Power System NSB 170FT/100FT Blue Plus

• Power Supply
   ‐Nominal Voltage(V): ‐54.5
• Power Distribution
   ‐Priority Load Under Voltage Disconnect (V): ‐43.2
   ‐Main Load Under Voltage Disconnect (V): ‐43.4 (only for leaf site), otherwise ‐44.0V or as per operational priority.
• Battery Parameters
   ‐Charging Mode: User Defined
   ‐Battery Type: User Defined
   ‐Charge Max Current (A): 270
   ‐Battery Disconnect Temperature (°C): 65
RBS 6000    ‐In Service Date: Date of BBS Installation/Replacement
TMR 6000 • Battery Type Parameters
   ‐Charging Voltage (V): ‐54.5
   ‐Increased Charge Voltage (V): ‐56.4
   ‐Equalize Charge Cyclic Interval (Days): 15
   ‐Equalize Charge Time (Hours): 6
   ‐Boost Charge Time (Hours): 6
   ‐Boost Charge Trigger Voltage (V): ‐46
   ‐Nominal Temperature (°C): 25
   ‐Temp. Compensation Max Voltage (V): ‐55.7
   ‐Temp. Compensation Min Voltage (V): ‐53.5
   ‐Temp. Compensation Voltage Slope (V/°C): ‐0.048
Emerson 100
Emerson 200
Power System Narada 12NDT100A
Narada 12NDT180
Vision CT12‐180X
• Power Supply
   ‐Nominal Voltage(V): ‐54.5
• Power Distribution
   ‐Priority Load Under Voltage Disconnect (V): ‐43.2
   ‐Main Load Under Voltage Disconnect (V): ‐43.4 (only for leaf site), otherwise ‐44.0V or as per operational priority.
• Battery Parameters
   ‐Charging Mode: Automatic
   ‐Battery Type: Type 01
   ‐Charge Max Current (A): 15% of Installed BBS Capacity (Must not exceed in case more than one BFUs per Site are installed)
   ‐Battery Disconnect Temperature (°C): 60
RBS 6000    ‐In Service Date: Date of BBS Installation/Replacement
TMR 6000
Power System C&D TEL 12‐210FGC

• Power Supply
   ‐Nominal Voltage(V): ‐54.5
• Power Distribution
   ‐Priority Load Under Voltage Disconnect (V): ‐43.2
   ‐Main Load Under Voltage Disconnect (V): ‐43.4 (only for leaf site), otherwise ‐44.0V or as per operational priority.
• Battery Parameters
   ‐Charging Mode: User Defined
   ‐Battery Type: User Defined
   ‐Charge Max Current (A): 20% of Installed BBS Capacity (Must not exceed in case more than one BFUs per Site are installed)
   ‐Battery Disconnect Temperature (°C): 60
RBS 6000    ‐In Service Date: Date of BBS Installation/Replacement
TMR 6000 • Battery Type Parameters
   ‐Charging Voltage (V): ‐54.5
   ‐Increased Charge Voltage (V): ‐57.6
   ‐Equalize Charge Cyclic Interval (Days): 30
   ‐Equalize Charge Time (Hours): 12
   ‐Boost Charge Time (Hours): 6
   ‐Boost Charge Trigger Voltage (V): ‐46
   ‐Nominal Temperature (°C): 25
   ‐Temp. Compensation Max Voltage (V): ‐57.6
   ‐Temp. Compensation Min Voltage (V): ‐51.8
   ‐Temp. Compensation Voltage Slope (V/°C): ‐0.12